lovinlife06

230V appliance

17 years ago

I have a 230V cooktop.I live in US and have a 220 outlet with 50amps. I had a commercial electrician come in to hook it up and whatever he did created a immediate failure.

He now tells me he thinks I need to get a transformer.Can you please explain to me the differences in US electrical supply versus the UK electrical supply.

Thanks in advance for your help.

Comments (14)

  • 17 years ago

    I think you need a different electrician. Cooktop made for use where, what country? Failure, what kind of failure? And why do you now believe that you can do what your "electrician" could not?

  • 17 years ago

    I have no intention of hooking this cooktop up. I love the DYI approach but I do no electrical or plumbing. Dont want my house to burn down or flood. I am just wanting to understand the problems that need overcome so that I can have a good conversation with an electrician and make sure the next one I hire understands what needs to be done. I don't want the trial and error approach as it will destroy my cooktop. Breaker blew and sparks flew at outlet.

  • 17 years ago

    "Breaker blew and sparks flew at outlet." = Get a new electrician.

    If this guy suggests a transformer because of that he needs to get a clue.

    You need to find a guy with a clue.

  • 17 years ago

    If you don't intend to provide enough information for someone to grasp your problem and offer advice, why bother asking? Are you trying to get a De Dietrich 308 or 309 installed?

  • 17 years ago

    Yes I fully get that I need to find another electrician.
    Manuel shows 4 options with diagrams.
    Common conn.
    3 phases with 1 zero connection (3 IN a.c. 400V?50 HZ)
    2 phase and 2 zero connection (2 2N a.c. 230V/50 HZ)
    Special connections
    single phase(1IN a.c. 230V/50Hz)
    3 phase, no zero connection(3a.c. 230/50Hz)
    not de dietrich - Atag

    5 connection points plus the ground
    bridges are provided to combine connections.

  • 17 years ago

    Enclosed is some old info about wiring. You may have better luck asking on the appliance forum if you have a variant of the DD and you can touch base with folks who use them and pick their brains for wiring information. The terminal block picture along with the small wiring diagram basically show what is involved on a DD. The input power is going across the cooktop isolated transformer primaries. Instead of a British 230v wire and a neutral wire coming in from the street, you connect a black hot and a red hot where needed, with the street side input neutral wire connecting to ground.

    I would suggest that you are not going to have much luck with licensed electricians unless you can tell them exactly what must be done and insist that is only what you will accept. The tripping of breakers, "imported stuff not working here", "don't understand the instructions", is sometimes a diplomatic way of letting you know that "I won't do this and I'm leaving now".

    Here is a link that might be useful: Background to wiring

  • 17 years ago

    After seeing the following statement in the link you provided I stopped reading it...

    "In US circuits, ground and neutral are the same thing, just redundant. They both go to ground. The neutral wire, in most ciruits is a heavier gauge than the ground wire, which is why I prefer to cap the ground and use the neutral, but you can do it either way."

    Also I typically do not take advice from a homeowner on how to properly install the wiring to a cooktop - after all if they knew how to correctly install it they would do it themsleves. Demanding that something be done this way or the highway will basically leave you with the best and most knowledgeable people hanging up on you.

  • 17 years ago

    My Dutch is a bit rusty but looking at the power diagrams of manuals in the link show terminals 1,2,3 in various configurations are for British power (your case black wire 115v) going in for the burners and 4,5 are British neutral (in your case red wire 115v to provide a total of around 220v).

    It is easy for people to get confused and there were lots of examples of trades folks trying to install induction units in the early days who couldn't get their heads around the idea of connecting power to a "neutral" terminal. Let us hope your next installer has more up to date knowledge.

    Good luck

    Here is a link that might be useful: Atag Manuals

  • 17 years ago

    Thank You much for the info. My electrician is a neighbor who is licensed and working as an electrician. I asked to do work that was obviously outside of his comfort zone of what he is familiar with. He told me he had wired for and installed European appliances into a restaurant so I thought it was a good match. He is very nice guy and seems he was trying to help even though he was unsure of how to wire. We are doing a bit of work on the house and have been trying to hire professionals who live in our rural area or attend our church as times are so hard for the contruction industry and seems good to help our local guys. Usually is good for them as well as me.
    Thx to all who responded.

  • 17 years ago

    From link above:
    "In US circuits, ground and neutral are the same thing, just redundant. They both go to ground. The neutral wire, in most ciruits is a heavier gauge than the ground wire, which is why I prefer to cap the ground and use the neutral, but you can do it either way."

    What total BS.
    Dangerous BS.

    The neutral wire is a part of a 120 V circuit.
    It is not required for a 240 V load.

    They are not redundant, but perform very different functions.

    The ground (green or bare wire) is a safety ground.
    It is intended to allow enough fault current to flow if a hot conductor touches the frame of the appliance or tool.
    No current should flow on the groundING conductor if the equipment is operating correctly.

    The neutral (groundED conductor) is required for a 120 V circuit and serves as a current carrying conductor.

    A true 240 V load does not require a neutral.
    In the US system it requires the two hot legs of a 120/240 V single phase service to be connected.

    "single phase(1IN a.c. 230V/50Hz) "

    This is the connection the OP should be using.

  • 17 years ago

    Will this appliance work on 60hz current? Is it UL or ETL listed for use in the US?

  • 17 years ago

    lovinlife06, if you haven't gotten fed up and left already due to the attempts to insult you and your electrician...

    The underlying problem here has nothing to do with a voltage mismatch. We don't have 220 here in the US, we have 240, and an appliance designed for 230, especially a heating-type appliance, won't have an issue with that.

    A transformer would be used to match the voltage. You don't need to match the voltage. The tripped breaker and light show were due to some wires being attached the wrong way.

    Your electrician made a mistake. I won't fault him for that. I was reading about this on a "Non-US" electrical forum, some european appliances have multiple voltage configurations more complex than some of our dual-voltage motors do, which is necessary for the wide variety of voltages and wiring methods used in foreign countries. No doubt "Wire it this way for use in the USA" was not on the paperwork that came with it.

    If you'd like to photograph/scan the diagram included with the appliance, I'll bet I can send you back enough information for your neighbor/electrician to get it hooked up and working, sans fireworks.


    Oh, and you should definitely question the accuracy of that other link up there...

  • 17 years ago

    "A transformer would be used to match the voltage. You don't need to match the voltage. The tripped breaker and light show were due to some wires being attached the wrong way."

    No transformer is needed.
    Hook the itme up as single phase 240 V.

    The 60 Hz may cause clocks and motors to run at a faster rate, but running a 50 Hz motor on 60 Hz will not harm it.

    Running a 60 Hz motor on 50 Hz can saturate the iron core and cause overheating.

  • 17 years ago

    ""In US circuits, ground and neutral are the same thing, just redundant. They both go to ground. The neutral wire, in most ciruits is a heavier gauge than the ground wire, which is why I prefer to cap the ground and use the neutral, but you can do it either way.""

    More dangerous and incorrect advice from some bozo who probably thinks electrical work is no big deal.
    People should stick to their fields of expertise when giving out advice!!!

    aliceinwonderland_id, if you read this PLEASE STOP giving out electrical advice!