Hi all, I have a main panel in my house that was pigtailed from aluminum wire. All the wires going into the panel are copper romex, going to junction boxes in my attic where they switch to aluminum, and of course crimped at all outlets.
My question - The electricians used 12/3 wire from the junction boxes,tying circuits together, to the panel, it makes sense because it saves wire. The red and black hots go to seperate 20 amp breakers, no tie. They are all located right next to eachother, on the right side of my panel. Is this correct? Would that put them on seperate legs? I've added 240 circuits, as well as 120 circuits, to this panel, do I need to be concerned with where I put those as long as I don't touch the multiwire circuits?
I hope I made this clear and didn't ramble too much. Thanks for your time.
Ryan
davidandkasie
joed
Related Professionals
Tampa General Contractors · Winona General Contractors · Odessa General Contractors · Magnolia Home Remodeling · Fort Myers Home Remodeling · Shreveport Home Remodeling · Spring Home Remodeling · Muncie Home Remodeling · Saint Cloud Home Remodeling · Binghamton Home Remodeling · Manhattan Home Remodeling · Los Angeles Home Remodeling · Scottsbluff Home Remodeling · Middletown Bathroom Remodelers · Tucson Bathroom RemodelersabchoppersOriginal Author