I just removed my 40 year old gas oven and noticed the hidden outlet the oven was using (ignition and interior light). I'm replacing the oven with a double and adding a microwave.

The existing oven outlet isn't dedicated at all. The fridge, the gas range and the OH exhaust fan are the three things on that circuit. So I'm going to add a new box with yellow romex for 20a circuit right next to the old one. An electrician and I already pulled the yellow wire between the same stud space as the new #8/3 for the 40a oven, but the yellow is in the wall and obviously not hot yet.

https://onedrive.live.com/redir?resid=CBB4716C1C47FE7D!959&authkey=!AEa_z4opXl0bL2A&v=3&ithint=photo%2cjpg

1) Is there code to where the new outlet should NOT be placed (see pic). I was thinking to left stud of where the 40a box is (by the burn mark).

2) Is it better to remove the existing outlet and make it a junction, connect and cap the neutrals together, the hots together? Or just leave the old where it is even with a new one right next to it.

I didn't want to rewire the existing as it's stapled everywhere up the studs and a pain to work with.

Thanks.

Comments (5)

  • 11 years ago

    The boxes should have covers even if they're hidden behind appliances. It's not "better" nor worse to remove an unused receptacle. There's no requirement that there this circuit be dedicated (provided the installation instructions for the appliance didn't specifically call this out).

    There's not any particular place that matters if you're going to put it behind the oven, make sure the cord for the oven can reach it. While nothing precludes a cord and plug connected wall oven, most these days tend to just have appliance whips that mount to the box directly.

    cebury thanked Ron Natalie
  • 11 years ago

    Some new appliances that plug into a receptacle will have a recommendation on where the receptacle should be located. For example, my GE dual fuel range included a diagram that showed the gas connection on one side and the 50 amp power receptacle on the other side, and there is a curve/inset on the lower back of the oven that allows the space to clear these connections. If the connections were installed somewhere else on the wall I might not be able to push the range all the way back.

    bruce

    cebury thanked Bruce in Northern Virginia
  • 11 years ago

    Correct, when the manufacturer says required, it is required. If they just say it's recommended, you probably should follow that recommendation. Often, the placement recommendations are pretty practical matters as it indicates where there may be recesses or other practical matters in the back of the appliance that makes it a good idea to mount box in that position.

    I put an 48" "professional" range in one time and I had to move the box to fit the recess that I hadn't noticed was an issue in a casual reading of the instructions.

    cebury thanked Ron Natalie
  • 11 years ago

    Are you moving the oven location? Would a gas oven be usable there in the future? If not, I would make that existing box into a junction so someone didn't plug the microwave into that by mistake. Otherwise, if the space could hold a gas range in the future, I would label one outlet gas range and the microwave outlet as microwave.

    cebury thanked Vith
  • 11 years ago

    Thank you all. The new oven had specs for placement of the box, it is within the designated area.

    A gas oven would be usable there later, but very unlikely as the cutout width has been changed to support 30" electric and all affordable gas ovens are 24".

    I went ahead and converted the old outlet to a jbox with cover and installed a new dedicated next to it. New oven slid n perfectly. So far so good.