How to correctly wire this Dimmer Switch?

4 years ago

Happy new year everyone! Recently, I found out that the attic light and outlet are not working. After investigating the issue, I narrowed it down to incorrect dimmer switch installation. As you can see from the wall image, there are 3 black wires. One runs from the circuit breaker, and on its way, it feeds multiple switches in the laundry room. The second, runs from the attic. And the third, runs to the kitchen lights. This is very confusing since I'm not sure what's the purpose of the red wires, if the dimmer requires a Single Pole or 3-way installation, in addition that most instructional videos I watched had probably only one black wire coming out of the wall. I also attached another image of the dimmer switch wires. I'm thinking to connect all black wires together, but then what to do with the red wires since there are no red wires coming out of the wall? Any help would be greatly appreciated.

Comments (10)

  • 4 years ago
    last modified: 4 years ago

    "The second, runs from the attic."

    What is this wire connected to in the attic? You wrote that the black wire from the circuit breaker is connected to laundry room switches in addition to this one. Is there an outlet or switch in the attic that also receives its power from this circuit? If so, then follow the Single-Pole instructions:

    • Connect black wire from circuit breaker AND black wire to attic to the black wire on the dimmer.
    • Connect the black wire from the lights to the red wire on the dimmer.
    • Connect the ground wire to the yellow+green wire on the dimmer.
    • Cap the red+white dimmer wire.
  • 4 years ago

    I followed the instructions and the attic light and outlet are back. Thank you. Now the problem is that the kitchen light (connected to the red) is not working. I tested the red wire with a non-contact voltage detector, but it's getting none.

  • 4 years ago

    Bypass the dimmer by connecting all three black wires together. Does the kitchen light turn on?

  • 4 years ago

    Yes, the kitchen light works, but the switch doesn't. Does that mean it's dead?

  • 4 years ago

    I can't read the photo of the instructions, but what do they say about the two red wires on the dimmer (I assume that's what I'm seeing in the bottom photo)?

  • 4 years ago

    In a Single-Pole scenario it says, "connect the red dimmer wire to the load wire removed from the switch". In case of 3-way, "connect the red dimmer wire, red and white dimmer wire to the remaining 3-way switch's two wires removed from the switch.

  • 4 years ago

    One of your black wires feeds the kitchen light and another black wire feeds the attic. The third black wire is the power from the breaker panel. To find out which is which, if you are comfortable doing so, you can remove the dimmer and separate the three blacks and make sure they don't touch each other nor anything else. Make sure no kids or pets are around, and turn the circuit breaker back on. Check CAREFULLY which one of the three blacks is hot. CAREFULLY mark this wire, and shut the power off. Connect one of the two remaining blacks with the one you just marked, and turn power back on. Note what is now on: kitchen light or attic. Turn power off. Identify this wire accordingly. The remaining black wire feeds whichever did not get power in the previous step.


    The wire that you have identified as feeding the attic should be twisted together with the black wire you have identified as the power from the circuit breaker and the black wire from the dimmer switch. The red from the dimmer switch should be twisted together with the remaining black wire. Keep the red with a white stripe capped and the green/yellow connected with the bare ground wire.

  • 4 years ago

    "Yes, the kitchen light works, but the switch doesn't. Does that mean it's dead?"

    Maybe. What is the brand and model of the dimmer, and what kind of bulb does the kitchen light have (LED, fluorescent, incandescent)? They may be incompatible.

  • 4 years ago

    MEW-DM660 dimmer switch + Recessed LED lights. They used to work just fine until I noticed the issue in the attic. I'm thinking I might have blown it out because while trying to wire it earlier, before posting here, the circuit breaker tripped immediately after turning it on.

  • 4 years ago

    Yeah, the Maxxima MEW-DM660 looks like it should work if your LED light is more than 4.5 watts as noted in the instructions AND IS DIMMABLE. I use Lutron LED+ dimmers; you might try the Lutron CTCL-153PDH-WH Skylark Contour LED+ Dimmer Switch -- if you need a replacement.