Tripping breaker

8 years ago
last modified: 8 years ago

I have a light switch that powers a post light in front of the house (with an outlet on it) as well as two other outlets on my deck. Went out one evening recently and when we got home the light was not on. I really thought I had turned in on before leaving. I had. Tripped breaker.

Even with no bulb in the socket (I used air to make sure the socket was clear of moth wings, etc, and nothing plugged into any outlet, the breaker still trips the instant I turn on the switch. This has been in place for 10 years probably. Nothing has been done to it (no modifications, no other work even remotely close to it). Power to the two outlets run in the crawl space under the deck. The line to the post lamp is underground in conduit.

Could it be the breaker itself? That would be the easy way out I know. Other than going under there and taking legs out of the circuit (yuck) any other advise?

Thank you!

Comments (7)

  • 8 years ago

    Doubtful it is the breaker. Most likely there's a wiring fault in the box that contains the switch or possibly where the light fixture is.


  • 8 years ago

    To rule out the breaker, I'd move the connection to another in the panel.

  • 8 years ago

    With the breaker off, (open, tripped, etc.) take a multi-meter and read resistance between the two prongs in the socket. Should be infinite. Just as second check, take a resistance reading between the "hot" socket prong - the thinner, "non polarized" one and the ground terminal (the round-ish, D-shaped one) - should be infinite. If not infinite in these readings then you have a direct hot wire to ground short. Since you're there, a resistance reading between the "polarized" socket prong and the ground socket prong short be minimal (like, ideally zero ohms). Check all other outlets for signs of water/bugs/nests/contamination by popping the outlet cover off for a visual inspection.

  • 8 years ago

    Defective breakers that trip for no reason are rare.

    Worst case scenario here: the person who buried the cable didn't screen the backfill and a rock has damaged the cable.

    If you disconnect everything at both ends and your ohmmeter reads something less than infinity across any two wires in the cable, it's a bum cable.

  • 8 years ago

    Morning all. Thanks for the advice and comments. Issue is resolved. I found a broken ground in the circuit in one of the outlets. It was a good opportunity to inspect everything, since it's outside. Took it all apart, then put each leg back in and tested one at a time.

  • 8 years ago

    That's great! Nice job in being thorough with your inspections. It's worth the effort to check things over, even if nothing wrong is found, at least peace of mind is!