Insufficient cooling Carrier 42000 BTU R22 scroll compressor
bighank
9 years ago
Have a Carrier scroll compressor R22 3 1/2 ton unit outside and a 4 ton piston coil inside at furnace. R22 charge is 7 pounds. Original coil was a thermal expansion type but was leaking R22 and was replaced with a piston type 4 ton coil about 2 years ago. Cooled fine for 2 years. Started AC intermittently 2 days ago as humidity is high and temp only in the 80s. Now noticed that air coming out of 1st floor outlets not very cold.
Pressures measured at charge ports on the compressor are 140 PSI on the high side or compressor output and 97 PSI on the low or suction side of the compressor.
High side tubing is not hot and low side tubing to the inside coil is not cold.
Coil is not very cold either as I accessed it thru the holes where a humidifier is used in the winter with the furnace.
Are these pressures OK for R22 with ambient air temperature of 88 degrees F?
What are potential causes for insufficient cooling given the data supplied above?
jakethewonderdog
clocert
Related Professionals
Gardena Solar Energy Systems · Sun Prairie Solar Energy Systems · Saratoga Springs Solar Energy Systems · Azalea Park Solar Energy Systems · Ashburn Home Automation & Home Media · Berkley Home Automation & Home Media · Brookfield Home Automation & Home Media · Clearwater Home Automation & Home Media · Fort Collins Home Automation & Home Media · Norwalk Home Automation & Home Media · Ocala Home Automation & Home Media · Ponte Vedra Beach Home Automation & Home Media · Robbinsdale Home Automation & Home Media · Ashland Electricians · Puyallup Fireplacesklem1