Need help troubleshooting HVAC problem

john617golden
8 years ago

I have two Goodman units. One 3 ton for main floor and one 2 1/2 ton for walkout basement. The units were installed new in late 2013. Last year each compressor had to be replaced under warranty. Now the upstairs unit is not cooling properly. The company I purchased the units from is telling me I need window treatments before he can really help me. We have a wall of windows overlooking a lake.

I got a second opinion. The 2nd guy is concerned about the pressure readings, 165 on low side and 290 on high. He tried to pump the system down to replace a part and the compressor wouldn't go below 80 psi.

He is also concerned that we don't have adequate return air supply for the units. Both air handlers are in the basement area and are tied to the same return air duct. The duct has a 16" diameter opening on one end and a 12" x 12" opening on the other.

Do these facts ring any bells for anyone?

Thanks

JG