We would like to start building our own house in about 5 years. We are on the edge of zone 5a and 6. Our interior insulation will be mineral wool r23, then 1/2 plywood sheathing. Here is where the debut comes in. I would like to put 3/4 rigid board insulation on the outside to help with thermal bridging and to help as an air barrier. Questions on house wrap.
1. If we put it on under the rigid board, it helps get any inside moister away from the sheathing, but you're letting the outside moister further in. If you put it on over the board your stopping the outside moister before it gets to the rigid board keeping it further away from any wood, but could inside moister get trapped between the sheathing and rigid board? Should you do 2 layers? It's relatively cheap right, about $300 to do a house? Why not do one over and one under the rigid board.
2. Last question, we are probably using vinyl siding (least maintenance). Use furring stripes to create an air gap or does vinyl siding have enough airflow to create a good drying situation?

Thank you everyone!
Ryan

Comments (10)

  • PRO
    PPF.
    5 years ago
  • PRO
    Summit Studio Architects
    5 years ago

    PPF is right. The Building Science website can explain how the 3/4" rigid insulation can create conditions for moisture to condense in the wall as the warm, humid indoor air reaches the dew point in the batt insulation. You need more rigid insulation and less batt insulation. The consensus seems to be that 30-50% of the R-value should be rigid insulation.


    I have actually gone back to 2x4 construction with R-13 batts and 2" Zip-R (R-9). You may need to go with 2 1/2" Zip-R (R-12) depending on the code version your building department uses. This combination saves a little in framing, has a good balance between permeable and non-permeable insulation, and has excellent thermal performance.

  • rjwassink67
    Original Author
    5 years ago

    Thank you. I have been looking on there and can't seem to find anything. Wow, there is a lot of info. Sorry, for needing it simple, but where would I look? Thank you

  • worthy
    5 years ago
    last modified: 5 years ago

    No need for housewrap--which is virtually never installed 100% properly--if you use tongue and groove XPS (extruded polystyrene) with taped seams.

    See here for explanation of minimum thickness of exterior insulation by climate zone.

  • rjwassink67
    Original Author
    5 years ago
    Wow, might rethink using outside rigid board. that is a lot of insulation
  • worthy
    5 years ago
    last modified: 5 years ago

    As per the IRC Table, only 1"-1.5" of XPS if you insulate to the minimum requirement.

    ( Boards less than an inch thick will easily snap in two if caught by a breeze on site.)

  • ulisdone
    5 years ago

    You want to use 2 layers of foam board with taped staggered seam, regardless of thickness.

    The link that worthy posted above is also a good site for education: Green Building Advisor.

  • PRO
    Charles Ross Homes
    5 years ago

    My suggestion is to defer the decision until closer to the time you'll be building. In five years, your project will be subject to a new edition of the building code, plus, products like Huber's Zip-R sheathing will have five more years of installed performance history so you can make a more informed choice at that time.

  • worthy
    5 years ago
    last modified: 5 years ago

    The free 2010 article Worthy links....

    Holladay updated it to 2016.